Be part of our community & join our international next generation forum now!
Months ago I purchased all the parts to change my box to 4-20ma prop valve. Cant seem to get it to hold temp. Has lots of over/under shoot. I know a few people have this sort of setup and i am curious to know of its performance. I can tune it to hold reflux and the minute I set on a new temp its completely out. Its a pretty slow valve but I think its similar to @CothermanDistilling's IE Johnson valve. It occurs to me that the controller might be the issue its a rexc700 if a better controller might give me a better result I would definitely grab a replacement but if this is the expected performance I would choose to go back to a solenoid which I know to hold temp within .5c
Comments
Can you set it to manual?
If so what is the flow rate at 100% and what is the max power going into the boiler?
I can set it to manual but I have nothing to measure it with. I have been using mains water and a gate valve to adjust water flow. System is running around 7kw its a 5" still. When I am next in the shed I can grab a jug and stopwatch and work it out?
How about a drum, bathroom scales and a one minute timer.
Don't change out the PID, it won't make much difference.
What valve do you have (specific model)? What flow rate range are you targeting? Where is the temp probe? What are your P, I, and D values?
At 7kW I would suggest anything that gives over 4 or 5l/min is a bit big. How much over 5l/min suggest how much too big.
To work out the bare minimum water required just use,
60 * (kW-loses) / (SHw * (Tout-Tin)) = flow rate in l/min
kW = power to the power.
loses = heat lose for your system in kW. Mines about 0.300 kW
SHw = Specific Heat value for water, 4.185
Tout = Put the lowest vapour temp which would be about 75°
Tin = What’s the highest feed water temp you might use, say 35°
60 * (7-0.2) / (4.185 * (75-35)) = 2.4 litres a minute to get 100% reflux so the valve needs to adjust less than this to start taking product.
This assumes a very efficient heat exchanger (deph) that will get the water close to the vapour temp.
Loses will be will pretty consistent for your set up regardless of power settings. It's a function of the surface area and the DeltaT between air and still which is pretty consistent. You can measure it by lowering the power to the point where the take-off stops. At that point the power in is equal to the power out (loses).
Mine doesn’t have a lot of surface area (4x4" plates on an insulated keg)
If your bucket and stopwatch gains between 3 and 5 kg a minute of weight in a minute then you’ve got the perfect size valve.
You can compensate a bit with the p value in the PID but if it’s way off you’re pushing shit up hill from the start.
That’s why I think the flow rate is the first thing to check.
That should read 'to the boiler'. And heat loss under it. Perhaps a mod can fix it. Sorry English is not my stong point.
OK, first you need to list all your devices by model number, and any settings they have, then where the temp probe is and what kind of condenser you are using, pressure and temp of water, etc...
Note - I am looking at the manual (PDF) I found on google and do not see a way to set the minimum valve opening, if you have the probe outside the condenser, and no minimum flow, you will never get it to work right.
Sorry for the delayed response been a while since I have been in the garage and went down today to try another attempt. Measured out the flow and adjusted to 4L per minute with a gate valve. No improvement in the operation what I find is that the valve overshoots a great deal on the heating side of things. Stops up pretty well on the cooling side of things
Here are the details of the setup:
I have attempted a variety of other settings using the below method:
Not sure what to do next, put solenoid back into service while I nut out the issues.
OK, numbers look right... The only difference i see is that the sestos PID has a setting to have the current output set to a minimum value, I think I have mine at 77(7.7mA).. but since you have the probe in the condenser, that should not matter..
rexc700-FK02-8*AN
the F means reverse action, not sure about this, but should not be an issue, looks like it has more to do with fail-safe for spring return valves
The K02 means K thermocouple with 0-400C range.. so P value of 30 is 120C 'proportional band' the Sestos is -50-1300C , so 30 is 405C (P is inverse, the smaller number means faster reaction)... my suggestion would be to increase the P number
when you refer to the 'cooling side of things' and 'heating side of things', I am not quite understanding... I guess 'heating side of things' means you could be increasing power and cooling means decreasing power? On mine, if I go from 5500W to 11,000w to 16,500w and back, it takes a full minute or more to get the RV temp to the setpoint again, it may overshoot a degree or so and then comes to the setpoint... Maybe I should state that my goal is not to have the system control quickly for such a large change, but to stay at the setpoint over the course of the run, where the temp rises slowly... this also points to raising the P value and slowing the response.
This has been an interesting journey for me and all the adjustments and the like that I have taken to improve the performance of my proportional valve have improved the performance of my solenoid. I think the biggest improvement has been in setting the flow rate of my water to something that makes sense. Currently with a solenoid valve and prop valve side by side I prefer the solenoid as its performance adjusts almost instantly to what ever is happening. Living in a house with three women means that someone is always messing with a tap or using water. Thank you to everyone who chimed in with advice on this one and believe me when I say I am thankful and appreciative to finally have a solution which makes me happy.
-Voo
You were running a single solenoid on municipal water supply, correct?